For users requiring filtered ring main pressure air supply, two air filters with isolation valves shall be
provided in parallel before a distribution manifold.For users requiring filtered reduced air supply, two air filter regulators with isolation valves shall be
provided before a distribution manifold.Each branch off shall be provided with a 1/2″ isolation
valve.Minimum two spare branch off with valve and plug shall be provided for each manifold.
Air manifolds shall be provided with a drain isolation valve at lowest point.
Simplified air supply arrangements may be used for few and/or non critical consumers.