Sensors shall be unaffected by ambient conditions.
Fire and Gas detectors may be of the smart/addressable (e.g. field bus) type.
Detectors should have a self test system. This system should be automatically operated.
Smoke Detectors
Detectors shall not be sensitive to water vapour.
The application shall determine the detection principle to be used.
Detectors shall have local alarm indicators to visually indicate when detectors are in alarm mode.
Very early smoke detection system may be used for cabinets in LER’s.
Heat Detectors
Heat detectors shall not be installed unless no other detection principle can be utilised.
Heat detectors and settings shall be selected in accordance with NFPA 72E 3-3 Temperature classification.
Flame Detectors
Detector shall be of the IR or combination IR/UV type.
The application shall determine the type to be used.
Sensors shall not be susceptible to spectral response variation when subjected to continuous operation.
Gas Detectors
Line detectors (open path) shall be evaluated in combination with point detection.
IR detectors should be used.
Application shall determine if catalytic detectors should be used.