Instrument Installation Principles
-
Instrument Installation Principles
Pressure sensing instruments that can be clogged due to high viscosity fluids or hydrates or if the
measurement can be affected by other factors, shall be equipped with chemical seals.Pressure instruments shall have individual process isolation valves.
Combined solutions may be used when not causing operational disadvantage/safety reduction during
service of instruments etc.Each pressure instrument with process connection shall be fitted with an instrument block /bleed
manifold (2/5 – way valve).Full functional independence between control and safety devices shall be assured, including
vessel/pipeline connections (e.g. common pressure tap for control and safety devices shall not be
used).The use of combined manifolds for piping and instrument valves shall be evaluated.
Combined
manifolds should be used when instruments are direct mounted on or in the immediate vicinity of the
pipe/vessel.Package suppliers shall terminate hydraulic and pneumatic tubing at skid edge with bulkhead male
connectors or unions.Package suppliers shall terminate instrumentation cables in junction boxes at skid edge or at agreed
termination point.If safety and functional requirements are fulfilled, the following shall apply:
Field instrument process connection: 1/2 ” NPT ref. ANSI/ASME B1.20.1.
Field instrument pneumatic connection : 1/4 ” NPT
Field instrument hydraulic connection: 1/2″ NPT
Field instrument cable entry: ISO threads – size depending on cable size.