Sht20 sensor and plc on rs485 modbus communication

  • PLC

    Sht20 sensor and plc on rs485 modbus communication

    Posted by Lakshan narayanan on November 17, 2025 at 6:28 pm

    SHT20 temperature and humidity sensor with delta dvp12se11t rs485 modbus.

    Hello,

    I’m trying to connect the SHT20 sensor with my DVP12SE11 T PLC in WPLL software with Modbus RTU RS-485 connection to read the temperature and humidity sensor values. Here, I used the sht20 sensor model is MD02, but I wrote the PLC program at that address it’s reading the random values.

    Here I have attached the program.

    Jason Hogan replied 1 month, 1 week ago 2 Members · 1 Reply
  • 1 Reply
  • Jason Hogan

    Member
    August 20, 2026 at 2:29 pm

    Here is a clean, plain-text Markdown version with zero raw HTML attributes or LaTeX formatting so it renders perfectly without breaking the editor:

    Random values usually happen due to register address offsets or mismatched serial settings.

    Try these quick fixes:

    Check Register Addresses:

    Temperature: 0x0001 (or 1 Decimal).

    Humidity: 0x0002 (or 2 Decimal).

    Delta Tip: If the data looks wrong, shift the address down by 1 to 0x0000.

    Divide by 10:

    The sensor sends values scaled by 10. A raw reading of 255 means 25.5°C.

    Check COM Port Settings (D1120):

    Default SHT20/MD02 settings are usually 9600 baud, 8 data bits, No parity, 1 stop bit (8, N, 1), Slave ID = 1. Ensure D1120 in Delta matches this.

    WPLSoft Instruction:

    Use the standard read instruction: MODRD K1 H1 K2 (Slave ID 1, Register 0x0001, Read 2 Registers).